Clarification about "opening control entities" #926
-
Beta Was this translation helpful? Give feedback.
Answered by
jmcollin78
Feb 22, 2025
Replies: 1 comment 3 replies
-
Yes the opening degree is the entity that allows the direct control of the valve. This is number entity that force the opening of valve. And this is obviously mandatory else you cannot control the valve. As described in the documentation (https://github.com/jmcollin78/versatile_thermostat/blob/main/documentation/en/presentation.md#equipment) you should use the |
Beta Was this translation helpful? Give feedback.
3 replies
Sign up for free
to join this conversation on GitHub.
Already have an account?
Sign in to comment
You don't have opening degree entity so you cannot use the 'direct valve control' self-regulation.